NEC Legal? 30A Breaker with 12AWG and 20A Receptacle

Status
Not open for further replies.

Always4

Member
Location
Philadelphia
Occupation
Electrician
Based on principal:
15A- 14AWG
20A- 12AWG
30A- 10AWG

Is there a specific code reference that prohibits 12AWG NM Cable and 20A receptacles on a Single Pole 30A breaker?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are several NEC sections that would prohibit this. Here is two: {Table 210.21(B)(3)} {240.4(D)(5)}