When performing a SERVICE calculation, do you assume the lighting load to be at 125%?
I understand that branch lighting circuits are to be calculated at 125% of the connected load, but section 220-11 (and table 220-11) in the NEC say that the lighting load demand factors are at max 100% when calculating a service size.
Now, there's a good chance I'm intepreting it wrong, but I wanted to make sure because on service calculations for larger facilities, that extra 25% could be a couple hundred amps difference in main service feeder size. And with copper prices topping out, this can become a major issue.