I am trying to relocate a few breakers in a residential house from the main panel of a new construction. The loads include four 60A furnace breakers, two 30A water heaters, two 50A AC units, and a 30A dryer breaker, all of which I plan to move to a new panel. My goal is to keep the feeder breaker size to 150A. However, when I perform the load calculations for these appliances without knowing their actual wattages, I find it difficult to keep the total below 200A. The load calculations exceed I have a 200A service panel, but I'm only using certain appliances without including other general loads. Here’s how I can resolve this issue:
**Step 1:** Determine the larger of the two loads: 65% of the heating load or 100% of the AC unit.
**Step 2:** Consider general lighting usage as 0 since I am relocating no loads to the new panel.
**Step 3:** Small appliances also count as 0 because I am not relocating any loads to the new panel.
**Step 4:** For fixed loads, I have two water heaters at 4,500W each, totaling 9,000W, and one dryer at 5,000W.
**Step 5:** From Step 1, use the highest value. For Step 2, 3, and 4, take 100% of the fixed loads and the rest at 40%, which totals 9000W.
**Step 6:** Add the results from Step 1 and Step 5, then divide by 240.
The result is above 150A; I am sure this is not true as the actual demand is definitely less than 150A, but how can we prove on paper that the loads I am trying to relocate will be less than 150A?
**Step 1:** Determine the larger of the two loads: 65% of the heating load or 100% of the AC unit.
**Step 2:** Consider general lighting usage as 0 since I am relocating no loads to the new panel.
**Step 3:** Small appliances also count as 0 because I am not relocating any loads to the new panel.
**Step 4:** For fixed loads, I have two water heaters at 4,500W each, totaling 9,000W, and one dryer at 5,000W.
**Step 5:** From Step 1, use the highest value. For Step 2, 3, and 4, take 100% of the fixed loads and the rest at 40%, which totals 9000W.
**Step 6:** Add the results from Step 1 and Step 5, then divide by 240.
The result is above 150A; I am sure this is not true as the actual demand is definitely less than 150A, but how can we prove on paper that the loads I am trying to relocate will be less than 150A?