430.130 Branch-Circuit Short-Circuit and Ground-Fault Protection
for Single Motor Circuits Containing Power Conversion
Equipment.
(A) Circuits Containing Power Conversion Equipment.
Circuits containing power conversion equipment shall be
protected by a branch-circuit short-circuit and ground-fault
protective device in accordance with the following:
(1) The rating and type of protection shall be determined by
430.52(C)(1), (C)(3), (C)(5), or (C)(6), using the fullload
current rating of the motor load as determined by
430.6.
(2) Where maximum branch-circuit short-circuit and groundfault
protective ratings are stipulated for specific device
types in the manufacturer's instructions for the power
conversion equipment or are otherwise marked on the
equipment, they shall not be exceeded even if higher
values are permitted by 430.130(A)(1).
(3) A self-protected combination controller shall only be
permitted where specifically identified in the manufacturer’s
instructions for the power conversion equipment or if
otherwise marked on the equipment.