ron1k

Member
Could someone help in finding a code refernce regarding conduit size. We at a Water Reclamation Facility have contractors doing installations at remote pumping stations. This one contractor has changed conduit size in the run. He has changed 1 inch to 3/4 in which he pulled a comm. cable Belden multi pair. I can use the table for conduit fill based on the specs from Belden and also probably use art.110-12 Mechanical Execution of Work. Any other suggestions?
 
Re: NEC - need a code refrence

Limited energy cabling does not have to comly with raceway fill restrcitions. See 800.110 Exception.
 
Re: NEC - need a code refrence

You issue isn't the fill because low voltage won't apply to conduit fill. The contractor can not deviate from the contracted drawings/specs without approval for the engineer. Tell him to put the 1" in or give you a pare 3/4"
 