Does the NEC and/or NFPA 70E have jurisdiction within any Utility owned Substations i.e. Control Buildings, Meter Houses, etc... and if so what is the article?
The NFPA 70 (a.k.a. NEC) applies to places where it says it applies, outlined in the very beginning, Article 90.2 (A), then in (B) (5) it SPECIFICALLY excludes electric utilities.Does the NEC and/or NFPA 70E have jurisdiction within any Utility owned Substations i.e. Control Buildings, Meter Houses, etc... and if so what is the article?
I was told in a code refresher class last year, but I can't find the reference that NEC had expanded into control houses, relay building, etc.... even for utilities. I am familiar with your reference above but the instructor (who is no longer around to contact) had expanded the scope a little bit further. So I was curious if anyone else had knowledge of the reference he was referring to. Thank you.
90.2 Scope.
(A) Covered. This Code covers the installation of electrical
conductors, equipment, and raceways; signaling and communications
conductors, equipment, and raceways; and optical
fiber cables and raceways for the following:
(1) Public and private premises, including buildings, structures,
mobile homes, recreational vehicles, and floating
buildings
(2) Yards, lots, parking lots, carnivals, and industrial substations
(3) Installations of conductors and equipment that connect
to the supply of electricity
(4) Installations used by the electric utility, such as office
buildings, warehouses, garages, machine shops, and
recreational buildings, that are not an integral part of a
generating plant, substation, or control center.