I have a 100HP Pump in a MCC being controlled by a VFD.
The FLA of the Pump is 77Amp.
77Amp *1.25 = 96.25Amp so I would use a 100Amp CB.
When I look at Allen Bradley One Line Diagram for the same pump they put a 200Amp CB.
What am I missing? Do MCC use a different method for calculating OCPD.
I'm trying to understand how they get 200 Amp.
The FLA of the Pump is 77Amp.
77Amp *1.25 = 96.25Amp so I would use a 100Amp CB.
When I look at Allen Bradley One Line Diagram for the same pump they put a 200Amp CB.
What am I missing? Do MCC use a different method for calculating OCPD.
I'm trying to understand how they get 200 Amp.