What’s the best resource to find minimum overhead clearance above for bare ACSR 6.6kV cabling inside an operating industrial plant road access way ?


Sent from my iPhone using Tapatalk
 
It does not matter who owns the land what matters is who owns the conductors.
If they are utility before a service point NESC.
After the service point NEC.
See definition of service point article 100 NEC / NESC page 11 same def.
 