R Rai136926 Member Location seattle, wa Aug 5, 2015 #1 Is there a NEC requirement or other common or recommended practice for distance between Manholes for Medium Voltage system?
Is there a NEC requirement or other common or recommended practice for distance between Manholes for Medium Voltage system?
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Aug 5, 2015 #2 I don't think there are any code requirements. The distance limit is most likely to be driven either by a client requirement or a cable pulling tension calculation. I have seen client requirements of 300 feet and 500 feet.
I don't think there are any code requirements. The distance limit is most likely to be driven either by a client requirement or a cable pulling tension calculation. I have seen client requirements of 300 feet and 500 feet.