What if the AHJ says Class A protection is not required on EVSE based on the manufacturer's instructions?
The AHJ would have to provide a written 90.4 special permission...something that is very very rare.What if the AHJ says Class A protection is not required on EVSE based on the manufacturer's instructions?
The installation and use instructions shall not reduce the requirements within this code.
That is not true they would not have received a listing if it was an NEC violation and these instructions comply with 625.54The AHJ would have to provide a written 90.4 special permission...something that is very very rare.
If the first draft stands as published the following will be added to 110.3(B) to address these types of issues.
Were on the 2017 code here thats what they are listed to a 2017 625.22That is not true they would not have received a listing if it was an NEC violation and these instructions comply with 625.54
I learned from Mike's website here that thats what UL CCID20 or CCID5 is.625.22 Personnel Protection System
The equipment shall have a listed system of protection against electric shock of personnel.
A permission to eliminate a GFCI requirement in the code would always require a written 90.4 permission...nothing in UL or any other document can eliminate a code rule.That is not true they would not have received a listing if it was an NEC violation and these instructions comply with 625.54
Public Input No. 1440-NFPA 70-2023 [ Section No. 625.54 ]
625.54 Ground-Fault Circuit-Interrupter Protection for Personnel.
All receptacles and outlets installed for the connection of electric vehicle charging shall have ground-fault circuit-interrupter protection for personnel.
It didn't pass yet they rejected yours that was supposed to add clarity to the definition of outlet LOLA permission to eliminate a GFCI requirement in the code would always require a written 90.4 permission...nothing in UL or any other document can eliminate a code rule.
The listing has nothing to do with these code rules as the code specifies GFCI protection by location of the receptacle or outlet and the product listing standards do not look at that.
Also the code making panel accepted your Public Input #1440 which expands the GFCI protection to all chargers, both hardwired and cord and plug connected.
Because they said it is 100% clear now...just not to youIt didn't pass yet they rejected yours that was supposed to add clarity to the definition of outlet LOL
An outlet is not required to exist on an individual branch circuit funny how they rejected exactly what everyone was saying was true.Because they said it is 100% clear now...just not to you
What is that attachment from, what is the full context? Pretty useless for making any point when it's cut off like that.An outlet is not required to exist on an individual branch circuit funny how they rejected exactly what everyone was saying was true.
PI # for this?????An outlet is not required to exist on an individual branch circuit funny how they rejected exactly what everyone was saying was true.
That is not even close to what the panel statement actually said. Your PI would have said an individual branch circuit shall supply only a single outlet. The panel rejected it with a statement that says an individual branch circuit may supply more than one outlet.An outlet is not required to exist on an individual branch circuit funny how they rejected exactly what everyone was saying was true.