We have a disagreement as to conductor derating for ambient temperature. We have 75/90 degree C cable in conduit and 75 degree rated terminations(terminated at equipment in high ambient temp. area). The conductors in conduit are derated for ambient temp. and # of conductors in the conduit from the 90 degree column of 310-16. I contend that since the terminations are also located in the high ambient area, the maximum ampacity must be derated from the 75 degree C column. Other say the 75 degree rating is ok without futher derating. Who is correct?