pagano21

Member
Need some help Guys. I just landed 5 4inch pvc conduits in a tap box with a rack of meters. The inspector came out and said I need plastic bushings. Now I know what the code says about any wire over a #4 you need a plastic bushings. But as you wireman know, buy the time you get the lock nut on the 4 inch pvc male adapter the bushing only has a few threads and when you start pulling wire they will usally come off and the male adapters are plastic. I usally try to put them on after the wire pull if I can. Just need some feedback.
Thanks Mike
 

drg

Senior Member
Re: Nec PLastic Bushings

Article 300.4(F) has a alternative to the threaded bushing.

John
 
A

a.wayne3@verizon.net

Guest
Re: Nec PLastic Bushings

John you are talking about a box connector right
 

pagano21

Member
Re: Nec PLastic Bushings

He is talking about another insulating material that will keep the conductors away from the edges of the conduit . That is an alternate method

Mike P.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Nec PLastic Bushings

See if you can find OZ Gedney phenolic bushings. They are a hard (bakelite) plastic and don't burn through when you pull, plus the they thread on and stay on. They are a tad bit bigger than the plastic. There are different quality plastic as well.
 