I have a clean room AHU designed with 8KW heater and 10HP fan motor on VFD set at 70%.
208V, 3PH, 8 KW heater wired to 30A, 3P circuit breaker and 208V, 3PH, 10HP motor is wired to separate 30A, 3P circuit breaker in panel. Panel is feed from normal/emergency generator power thru Automatic Transfer Switch.
At Normal Power load, AHU runs fine with heater and blower motor works without tripping circuit breaker but when normal power is out and emergency generator starts thru ATS, BOTH 30A, 3P circuit breakers for heater and blower motor trips and AHU goes completely off.
After checking load on generator panel, we found total load of 40 KW on panel and size of Generator is 40 KW.
Is it possible due to overload on generator, high AMP makes VOLTAGE drop on generator which overloads BOTH circuit breakers on AHU and trips both circuit breakers?
Is there any NEC requirements to correct this problem?