I am working on adding office space to a manufacturing plant. I need a transformer to supply this space. 480V-208/120V. My secondary load is a 125A main lug 24 space panel feeding (18) duplex receptacles and (16) 110V LED fixtures. There will also be (4) 20A ptac units.
Choosing a transformer, I assumed 200A secondary.
sqrt(3) * 200A * 208V = 72 KVA --> 75KVA transformer
Should I need this big of a transformer? What does the NEC state about load currents in this environment? Also, calculations in 120V vs 208V?