NEC requirements for open-delta 3-phase service.

Status
Not open for further replies.

Sabbah

New member
Location
San Francisco
Hi all,

What are the NEC requirements for a 3-phase service where a 120/240 open delta transformer is being used? The site is mixed use (commercial and residential), with separate meters and panels. One service feeds the whole unit though.

Thanks!
 
There are no special requirements other than the identification of the high leg and not using "slash" (120/240) rated breakers on the high leg.
 
Code cycles later than the '08 you show as applicable by profile require "high-leg" panels to be legibly marked accordingly. Not a bad idea although not required by your Code cycle.
 