My question is this:

Is there a code requirement that states a minimum distance from a wall that a transformer must be installed. I have heard that a transformer must be installed a minimum distance of 6" from a wall. Please advise.

Thanks
 
Take a look at 450.9 and 450.21. There are different applications based on a few different factors.
 
I agree with Rob.

The required distance for ventilation will be marked on the transformer nameplate. 6" sticks in my mind as a pretty standard ventilation distance requirement for most dry type transformers that I have installed.

Chris
 
Installation Instructions

Installation Instructions

I have found the spacing info in the installation instructions of the transformer.
 
Yes... so I'm guessing there would be minimal clearance from the wall on which they are mounted... :grin:

Someone just needs to invent some sort of anti-gravitational device so electrical equipment can float in mid-air.

Then the electrician could wear an anti-gravitational tool belt and float up to work on the equipment. Minimal hazard of being grounded while working on energized parts :D
 
Ventilated transformers usually require 6".

Enclosed, non-vented transformers can be mounted on the wall. (These are usually the smaller transformers, but if you want to pay enough, I think you can also get large enclosed transfomers.)

Not sure, but there also may be differences in sealed, enclosed, and/or non-vented transformers.
 