NEC RV Park Calculations??

Status
Not open for further replies.

c.cole01

New User
Location
riverside, ca
Occupation
PV
I have a RV site that has 600 - 50a 120v sites on a 600amp service.

They want me you run load calcs for the site and I don't know how this amount of sites is possible. I calc that it should be 30 sites per 600a service per NEC 551.73(a)
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Yeah, they seem off a bit. Although with the newest load calcs and all 50a sites that won’t be utilizing the 50a recept maybe some engineer signed off on it?
 