Permanent wiring:
I have a 120VAC circuit with 1 pole 30 A breaker feeding a 30A hazardous receptacle. During harzardous operation only it is Class I Div II. When the harzardous comodity is removed, the area is an UNCLASSIFIED area which we perform maintenace.
When the area is UNCLASSIFIED, I need to be able to use the 120VAC with standard 5-20R/P devices for pressure washing and power tools (general maintenance). Plug in for a day and then remove the equipment at the end of day.
One Approach:
I would like to purchase a 20A GFCI portable box (Hubble-GFP20M), cut the standard plug attached and connect a hazardous plug. Does code allow this approach? Or where/how does it explain this issue?
The box and wire probably has 14 AWG wire. The argument is that the box and wire is expendable and replaceable. Assuming only 20A equipment can plug into the GFCI box (5-20R/P).
Reference: NEC 527.6 Temporary Wiring
15, 20 and 30 amp, 125 VAC receptacle.
Second Approach:
I was first going down the path - that the 30A breaker will not protect the 14 AWG wire, so I will need to increase the wire size to 10 AWG-30A. Thinking the 20A GFCI box will be a problem, I would put in a 20A breaker or fuse to protect it. This makes the best sense but is it necessary?
Thanks for the help in advance.
[ July 31, 2004, 12:33 AM: Message edited by: powersurge ]
I have a 120VAC circuit with 1 pole 30 A breaker feeding a 30A hazardous receptacle. During harzardous operation only it is Class I Div II. When the harzardous comodity is removed, the area is an UNCLASSIFIED area which we perform maintenace.
When the area is UNCLASSIFIED, I need to be able to use the 120VAC with standard 5-20R/P devices for pressure washing and power tools (general maintenance). Plug in for a day and then remove the equipment at the end of day.
One Approach:
I would like to purchase a 20A GFCI portable box (Hubble-GFP20M), cut the standard plug attached and connect a hazardous plug. Does code allow this approach? Or where/how does it explain this issue?
The box and wire probably has 14 AWG wire. The argument is that the box and wire is expendable and replaceable. Assuming only 20A equipment can plug into the GFCI box (5-20R/P).
Reference: NEC 527.6 Temporary Wiring
15, 20 and 30 amp, 125 VAC receptacle.
Second Approach:
I was first going down the path - that the 30A breaker will not protect the 14 AWG wire, so I will need to increase the wire size to 10 AWG-30A. Thinking the 20A GFCI box will be a problem, I would put in a 20A breaker or fuse to protect it. This makes the best sense but is it necessary?
Thanks for the help in advance.
[ July 31, 2004, 12:33 AM: Message edited by: powersurge ]