Ryan@graceelectric
Member
- Location
- Massachusetts
- Occupation
- Master Electrician
I have a question that has been bugging me for a while. Table 250.122 states that the equipment grounding conductor size for an overcurrent device of up to 200 Amps is a #4 aluminum. Why, then, does #4/0 SER aluminum cable come with a #2/0 aluminum equipment grounding conductor? I’ve been a master electrician for 20 years and have installed hundreds of services with this type of cable. I have also installed plenty of services in conduit where I have used XHHW AL conductors and ran a #4 aluminum equipment grounding conductor per 250.122 for residential services in the past where an external disconnect was required. This latest code cycle requires external disconnects in most, if not all situations, and we have been running across this apparent equipment grounding conductor sizing discrepancy more frequently, being that the main breaker panel is now wired as a sub panel.