timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
Just need some clarification for the NEC service entrance equipment for industrial facility. The utility supply at the point of interconnection (POI) is 12.47kV. After point of interconnection (POI), the scope of utility ends and the scope of plant starts. Then there is a 12.47kV fused disconnect switch (owned by plant) which feeds a 12.47kV-480/277V transformer, which then feeds a 480V switchboard. All the plant loads are fed by this 480V switchboard.
The neutral is to be connected to the ground at the service equipment.
What would be the service equipment in this case? Will the service equipment be the 12.47kV fused disconnect switch on the primary of the transformer, or will it be the 480V switchboard on the secondary of the transformer. Thanks.
The neutral is to be connected to the ground at the service equipment.
What would be the service equipment in this case? Will the service equipment be the 12.47kV fused disconnect switch on the primary of the transformer, or will it be the 480V switchboard on the secondary of the transformer. Thanks.