I am trying to figure out the service entrance neutral and ground conductors as per NEC. We have a delta-wye connected utility transformer, wye connected local standby generator, and a service entrance rated auto transfer switch (ATS), as shown in attached picture.
We don’t have neutral application, so we can remove the jumper between neutral and ground in ATS, and the cable-3 (ATS to MCC) would be a 4-conductor cable (L1, L2, L3, EGC). I have following questions.
Should cable-1 (utility transformer to ATS) be a 5-conductor cable (L1, L2, L3, N, GEC), or will a 4-condctor cable (L1, L2, L3, N) be enough?
Also, should cable-2 (Generator to ATS) be a 5-conductor cable (L1, L2, L3, N, EGC), or will a 4-condctor cable (L1, L2, L3, N) be enough?
Thanks