Hello folks,
I have a 20A lighting circuit with an actual load of 15A. Due to the length of the circuit and voltage drop considerations I will need to use a 1/0 conductor to reduce the voltage drop. The 20A CB can handle up to a #4 conductor.
I'd like to use a #12 conductor from the 20A CB in the panelboard over to a junction box, where I'll splice the #12 to a 1/0 conductor. Then down the line I'd splice a #12 from the 1/0 conductor over to the light fixture.
Is this acceptable within the NEC?
Thanks,
I have a 20A lighting circuit with an actual load of 15A. Due to the length of the circuit and voltage drop considerations I will need to use a 1/0 conductor to reduce the voltage drop. The 20A CB can handle up to a #4 conductor.
I'd like to use a #12 conductor from the 20A CB in the panelboard over to a junction box, where I'll splice the #12 to a 1/0 conductor. Then down the line I'd splice a #12 from the 1/0 conductor over to the light fixture.
Is this acceptable within the NEC?