I am not sure how to use Table 220.88 and cant find the answer I am looking for. I have seen Mike Holt do a calculation as referred to the note at the bottom of the table.
Question: What is the Calculated load for an all electric restaurant that has a total connected load of 325 kva at 120/208 3phase paralleled in 2 raceways. Size the Conductors?
First 200 kva at 80% and the remainder from 201 to 325 at 50%.
200 x .80 = 160
125 x .10 = 12.5
160 + 12.5 = 172.5
172.5/(208x1.732)=x
172.5/(360.3)=.4787
1000x.4787= 479 amps
479/2 (Raceways)=239 amps
Conductors per Table 310.15(B)(16) 75 degree C is 250 kcmil
The Grounded conductor per 250.24(C)(2) not smaller than 1/0
The Grounding Electrode Conductor per Table 250.66 (equivalent of the parallel conductors is 500 kcmil) is 1/0
Total Connected All Electric Restaurant
Load (kva) Calculated Loads (kva)
My question is in Table 220.88 where it states " 201-325 10% (amount over 200) + 160" where does the (amount over 200) + 160 come into play?
Question: What is the Calculated load for an all electric restaurant that has a total connected load of 325 kva at 120/208 3phase paralleled in 2 raceways. Size the Conductors?
First 200 kva at 80% and the remainder from 201 to 325 at 50%.
200 x .80 = 160
125 x .10 = 12.5
160 + 12.5 = 172.5
172.5/(208x1.732)=x
172.5/(360.3)=.4787
1000x.4787= 479 amps
479/2 (Raceways)=239 amps
Conductors per Table 310.15(B)(16) 75 degree C is 250 kcmil
The Grounded conductor per 250.24(C)(2) not smaller than 1/0
The Grounding Electrode Conductor per Table 250.66 (equivalent of the parallel conductors is 500 kcmil) is 1/0
Total Connected All Electric Restaurant
Load (kva) Calculated Loads (kva)
My question is in Table 220.88 where it states " 201-325 10% (amount over 200) + 160" where does the (amount over 200) + 160 come into play?