NEC Table 220.88 Optional Method-Permitted Load Calculations for Service and Feeder Conductors for New Restaurants
Hi all.
I am Manufacturing Plant Journeyman Electrician apprentice in Oregon. I am finishing up my schooling in a code class. We had a calculation to do last night in class and there was some confusion over this NEC table, and how to do the calculation.
The problem is as follows:
First Part: A new restaurant has a connected load of 324 kva, all electric equipment. What is the demand on the 3-phase 208/120v service?
According to the table this is my math:
10% (of amount over 200)+160
12.4+160=172
172/(208 x 1.732) = .47855 x 1000=478.55 Requires a 500 amp service.
Second Part: If the restaurant had NOT all electric equipment?
According to the table this is my math:
50% (of amount over 200)+200
62+200=262
262/(208 x 1.732) = .72727 x 1000=727.27 Requires an 800 amp service.
Is this right? If so why would a restaurant with the same load, but not all electric equipment require such a higher demand?
Thanks for the help.
Rob
Hi all.
I am Manufacturing Plant Journeyman Electrician apprentice in Oregon. I am finishing up my schooling in a code class. We had a calculation to do last night in class and there was some confusion over this NEC table, and how to do the calculation.
The problem is as follows:
First Part: A new restaurant has a connected load of 324 kva, all electric equipment. What is the demand on the 3-phase 208/120v service?
According to the table this is my math:
10% (of amount over 200)+160
12.4+160=172
172/(208 x 1.732) = .47855 x 1000=478.55 Requires a 500 amp service.
Second Part: If the restaurant had NOT all electric equipment?
According to the table this is my math:
50% (of amount over 200)+200
62+200=262
262/(208 x 1.732) = .72727 x 1000=727.27 Requires an 800 amp service.
Is this right? If so why would a restaurant with the same load, but not all electric equipment require such a higher demand?
Thanks for the help.