NEC table 310.15(B)(16) and wireways

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
All my life I have been using table 310.15(B)(16) to size wires that are going into a wireway...

Wireways are allowed to have 30 CCC without derating but how come we are allowed to use this table if this table is for "Not More Than Three Current-Carrying Conductors in Raceway"? By definition a wireway is a raceway.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Note 2 to Table 310.15(B)(16) (2020 NEC) says "Section 310.15(C)(1) shall be referenced for more than three current-carrying conductors." So the Note expands the applicability of the table to beyond what is in the title.

But section 310.15(C)(1) has no exception for wireways, so apparently the allowance of 376.22 is useless. Seems like an oversight.

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Note 2 to Table 310.15(B)(16) (2020 NEC) says "Section 310.15(C)(1) shall be referenced for more than three current-carrying conductors." So the Note expands the applicability of the table to beyond what is in the title.

But section 310.15(C)(1) has no exception for wireways, so apparently the allowance of 376.22 is useless. Seems like an oversight.

Cheers, Wayne
Just an example where a rule in one Chapter 3 article is intended to amend a rule in another Chapter 3 article, but there is no provision for that th happen in 90.3. However, I am not aware of any AHJ not permitting the applications of the provisions of 376.22(B) for wireway conductor ampacity adjustments.
 
Top