Gentlemen,
This is my first post here and I'd like to thank everybody in this forum who is providing help, I found already many great explanation for the NEC in here, kudos.
Now to my question:
Situation:
My thoughts:
Thank you for your replies!
Best regards,
Lukas
This is my first post here and I'd like to thank everybody in this forum who is providing help, I found already many great explanation for the NEC in here, kudos.
Now to my question:
Situation:
- I want to use two cables type "Gexol 37-102-317VFD" in parallel for the connection between the VFD and the motor this is a 2/0AWG and has the following temperature ratings: 110°C (201A), 100°C (188°C), 90°C (173A) & 75°C (145A) for an ambient temperature of 45°C.
- The motor has a rated current of 265A, no hp rating.
- My VFD has no temperature rating.
- The cable runs through 55°C ambient temperature.
My thoughts:
- cable needs to be 125% of 265A = 331,25A as per NEC 430.22
- as per NEC 110.14(C) my ampacity needs to meet the requirements for both the termination as well as for the cable insulation
- NEC 110.14(C)(1) & 110.14(C)(1)(b) tells me to look for the termination ampacity to Table 310.15(B)(16) column 75°C (above 100A) and not in the manufacturers spec sheet. As no correction or adjustment factor is used on the termination calulation, for 2 cables 2/0AWG that makes 2*175=350 > 331,25A -> looks good
Question #1: Does it matter that the cable spec sheet gives an ampacity of 145A@75°C? 2*145=290A < 331,25A -> doesn't look good - For "base ampacity" of the cable I use the manufacturers spec sheet: 2*201=402A > 331,25A
Question #2: Is that correct or do I have to use Table 310.15(B)(16), what is the spec sheet then good for??? - For temperature correction factor I use the equation given in 310.15(B)(2), as the table 310.15(B)(2)(a) doesn't have values for 110°C
SQUAREROT((110-55)/(110-45))=0,9198
Question #3: Am I using that equation correctly? - I have no adjustment factor for more conductors as my cable contains only 3 current carrying conductors and I space the two cables in my cable tray with one cable diameter distance as per 392.80(A)(1)(c)
- Makes an overall ampacity for the cable of 2x201x0,9198=368A > 332A -> looks good
Question #4: was all above correct?
Thank you for your replies!
Best regards,
Lukas