A askDano Member Location West Mifflin, Pa Dec 12, 2012 #1 I have a spec that calls for table 310-15(B)(22)(b), i could not find this in the 2011 code. Is it from an older rev and what is it now?
I have a spec that calls for table 310-15(B)(22)(b), i could not find this in the 2011 code. Is it from an older rev and what is it now?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Dec 12, 2012 #2 I thing itis in error. Call the engineer and see what he wants. I suspect he means 310.15(B)(2)(b) which is correction factors for ambient temps.
I thing itis in error. Call the engineer and see what he wants. I suspect he means 310.15(B)(2)(b) which is correction factors for ambient temps.