Hi, quick question...
I'm looking at an example for a coordination study and it mentions that we have a "3-1/C 500MCM". The solution then shows you a reference to table 310.16 (old NEC Ed) where they obtain the ampacity of 380A (circuit is 480v 3PH, installed in conduit).
Does table 310.16 (old NEC Ed) show ampacity for 3/C cables only? And would this apply also for 3 runs of 1/C cables installed in a triangular configuration?
Thanks,
Yogi