Hello,

i am having trouble understanding note 2 for table 312.6 (B). I don’t understand what it means by lay-in wire terminals intended for only one wire. Can someone elaborate this to me as I frankly can’t.

Notes 2:
for removable and lay-in wire terminals intended for only one wire, bending space shall be permitted to be reduced by the following number of mm (inches).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's a terminal that has the side either open or a portion of the terminal that is removable so that the conductor can be bent and laid into the terminal as opposed to pushing it into a closed terminal from the end of the terminal. Bonding bushings often have lay-in style terminals, some meter enclosures have lay-in style terminals where the fastening device can be removed.

Welcome to the Forum. :)

conduit-fittings-29523-64_1000.jpg


eaton-meter-sockets-unrrs213beuse-64_1000.jpg
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
A surface-mount range or dryer receptacle has lay-in terminals, too, where the plate with the screw swings out of the way.
 