NEC Table 430.250 power factor

Status
Not open for further replies.

patrox2000

Member
Location
Baltimore, MD
what power factor does table 430.250 use to calculate the FLA for the squirrel cage and wound rotor motors?

another question.

does the NEC require certain spare capacity when sizing panelboards or switchboards? or is this just good practice?

thanks to all in advance.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I don't think it is a calculation. They describe the numbers as being "typical." That sounds to me like empirical information, not calculated data.

The code does not tell us to maintain a minimum amount of spares. That is a design choice, or an owner's call.
 