Table 450.3(B) says "Maximum" rating or setting of OCPD
I have a 45kVA transformer (480/277V). Primary rated current would be 54.126 Amp
I have primary and secondary protection in my setup so 250% for primary and 125% for secondary per the table.
Question is... does it HAVE to be 250% as in 54.126 * 2.5 = 135.3 A resulting in 150A breaker for the primary?
Or can it be less, say 100 Amp?
I'm thinking less is acceptable since Table 450.3(B) says "Maximum".
What's throwing me off is that the NEC handbook examples are using the maximum for the example problems.
Thanks
I have a 45kVA transformer (480/277V). Primary rated current would be 54.126 Amp
I have primary and secondary protection in my setup so 250% for primary and 125% for secondary per the table.
Question is... does it HAVE to be 250% as in 54.126 * 2.5 = 135.3 A resulting in 150A breaker for the primary?
Or can it be less, say 100 Amp?
I'm thinking less is acceptable since Table 450.3(B) says "Maximum".
What's throwing me off is that the NEC handbook examples are using the maximum for the example problems.
Thanks