W wyboy Senior Member Jul 28, 2011 #1 Table 500.4 (A)showing allowable ampacity for SO cord only goes to size AWG. How is ampacity for larger SO cord calculated?
Table 500.4 (A)showing allowable ampacity for SO cord only goes to size AWG. How is ampacity for larger SO cord calculated?
Smart $ Esteemed Member Location Ohio Jul 28, 2011 #2 wyboy said: Table 500.4 (A)showing allowable ampacity for SO cord only goes to size AWG. How is ampacity for larger SO cord calculated? Click to expand... I think you meant Table 400.5(A). To answer your question, for an NEC compliant installation you cannot qualify SO cord larger than #2 without special investigation, per 400.4 and Table 400.4.
wyboy said: Table 500.4 (A)showing allowable ampacity for SO cord only goes to size AWG. How is ampacity for larger SO cord calculated? Click to expand... I think you meant Table 400.5(A). To answer your question, for an NEC compliant installation you cannot qualify SO cord larger than #2 without special investigation, per 400.4 and Table 400.4.
W wyboy Senior Member Jul 28, 2011 #3 Thanks! I?m not sure what ?special investigation? means. I assume it would be something the manufacture would have to do like a listing.
Thanks! I?m not sure what ?special investigation? means. I assume it would be something the manufacture would have to do like a listing.
Smart $ Esteemed Member Location Ohio Jul 28, 2011 #4 wyboy said: Thanks! I?m not sure what ?special investigation? means. I assume it would be something the manufacture would have to do like a listing. Click to expand... The term ?special investigation? is used twice in the NEC, in the same context. The NEC fails to incite its meaning.
wyboy said: Thanks! I?m not sure what ?special investigation? means. I assume it would be something the manufacture would have to do like a listing. Click to expand... The term ?special investigation? is used twice in the NEC, in the same context. The NEC fails to incite its meaning.