Upgrading an existing crane in a plant I am working on.
As part of this design the existing feeder is 250 MCM triplex aluminum. This is from a Motor Control Center to the exposed contact conductors.
I thought that a new cable would be required based on the ampacities in 310. It was brought up that possibly using table 610.14 would be acceptable to use smaller cables. I still felt a new cable would be required since the table does not cover aluminum.
I however also dont know when this table is applicable. Is it any time you are routing cables associated with cranes, or is it past the contact conductors. Do you use NEC 310 or 610 for sizing the initial cable from the MCC to the disconnect and the disconnect to the contact conductors.
Appreciate the help and clarification on this.
As part of this design the existing feeder is 250 MCM triplex aluminum. This is from a Motor Control Center to the exposed contact conductors.
I thought that a new cable would be required based on the ampacities in 310. It was brought up that possibly using table 610.14 would be acceptable to use smaller cables. I still felt a new cable would be required since the table does not cover aluminum.
I however also dont know when this table is applicable. Is it any time you are routing cables associated with cranes, or is it past the contact conductors. Do you use NEC 310 or 610 for sizing the initial cable from the MCC to the disconnect and the disconnect to the contact conductors.
Appreciate the help and clarification on this.