Is this 517.44(B)?
You are right. The issue is that you have paragraph (1) followed by an exception that itself has three conditions. The numbering should have resumed with (2) and not (4). Care to submit a suggestion for an errata? I don't know how to do that, but I am sure the NFPA web site has the process.Please correct me if i am wrong.
Manual transfer switch that connects power from a branch other than critical?Throw-over facilities. What does this mean?
You are right. The issue is that you have paragraph (1) followed by an exception that itself has three conditions. The numbering should have resumed with (2) and not (4). Care to submit a suggestion for an errata? I don't know how to do that, but I am sure the NFPA web site has the process.
Dang, sleem highlighted it and all, still blew right past me.:slaphead:
Aside from numbering, I see also number.5 has nothing to do with equipment branch as in 517.44(B).I missed it too.
.........
Obviously not the intent.
Dang MS word and their auto numbering.... I can never get what I want out of it either.....
Aside from numbering, I see also number.5 has nothing to do with equipment branch as in 517.44(B).
Looking at 517.35 as a guide, the exceptions should have been (a), (b), (c) instead of (1),(2),(3). That's probably why the numbering is off.
Some very odd changes to this section for nursing homes and limited care facilities. For one thing, referring to figures 517.42 (a) and (b), the "Critical Branch" is gone, and is now apparently called the "Equipment Branch".
So number 5 seems to refer to something that no longer exists in the new code??
However, 517.44(A) refers to the equipment branch, and 517.44(B) refers to the critical equipment branch. What the heck does that mean?