Gentlemen,
I am new to this forum and also not a NEC Code user in day-to-day work. I am working outside North America. We use IEC 60364/IEE 16 th edition etc. for conductor sizing and other IEC stds/recommendations. But I am interested in clarifying the following issues with reference to NEC.
As an example we need to size a branch circuit (3 core cable with 90 deg insulation material, directly buried), which is about 1500 feet long, and having a continuous current of say 250 Amps at an ambient temperature say 30 deg C at 480 Volts (we have got 400 Volts). If I am not mistaken, we can get the size from Table 310-16. It will be AWG 4/0. Now,
1) Since there is no table in the NEC which gives the voltage drops for different sizes, how do we make sure that 1500 feet long cable will not give more than 3% drop from 480 V input supply? ( FPN #1 of section 310-15 of NEC 2002 says that the ampacities given are without voltage drop considerations. North American manufacturers are also not publishing d.c resistance, a.c. resistance, reactance & voltage drop details of cables in their product catalogues. But the same is freely available with leading European manufactures.)
2) Since there is no table in the NEC how do we make sure that the conductor is properly sized for the short circuit current? (the 3-phase bolted fault current at the end of the cable is say 25 kA )
3) Why it is a practice in North America to use bare copper conductors as grounding conductors? (It is against our national codes to use them and should be with insulated conductors having green/yellow stripes. Bare copper can be used only in overhead transmission lines)
These may be very simple issues for NEC code experts in this forum. I honestly welcome them to explain these issues to a non NEC user.
Thanks in advance!
Chandra
I am new to this forum and also not a NEC Code user in day-to-day work. I am working outside North America. We use IEC 60364/IEE 16 th edition etc. for conductor sizing and other IEC stds/recommendations. But I am interested in clarifying the following issues with reference to NEC.
As an example we need to size a branch circuit (3 core cable with 90 deg insulation material, directly buried), which is about 1500 feet long, and having a continuous current of say 250 Amps at an ambient temperature say 30 deg C at 480 Volts (we have got 400 Volts). If I am not mistaken, we can get the size from Table 310-16. It will be AWG 4/0. Now,
1) Since there is no table in the NEC which gives the voltage drops for different sizes, how do we make sure that 1500 feet long cable will not give more than 3% drop from 480 V input supply? ( FPN #1 of section 310-15 of NEC 2002 says that the ampacities given are without voltage drop considerations. North American manufacturers are also not publishing d.c resistance, a.c. resistance, reactance & voltage drop details of cables in their product catalogues. But the same is freely available with leading European manufactures.)
2) Since there is no table in the NEC how do we make sure that the conductor is properly sized for the short circuit current? (the 3-phase bolted fault current at the end of the cable is say 25 kA )
3) Why it is a practice in North America to use bare copper conductors as grounding conductors? (It is against our national codes to use them and should be with insulated conductors having green/yellow stripes. Bare copper can be used only in overhead transmission lines)
These may be very simple issues for NEC code experts in this forum. I honestly welcome them to explain these issues to a non NEC user.
Thanks in advance!
Chandra