Carultch
Senior Member
- Location
- Massachusetts
I have a design in Massachusetts, which is taking credit for the Massachusetts-specific values that override Table 310.15(B)(3)(A).
http://www.mass.gov/eopss/docs/dfs/osfm/cmr/527cmr12-00.pdf
NEC values are more conservative than Massachusetts values. For 43 and above wires, Massachusetts allows 50% derates, while the NEC requires 35% derates.
Does this table apply to all circumstances where numerous conductors are in the same raceway, in Massachusetts? Both continuous and non-continuous loads, regardless if the circuit operation is simultaneous or diverse?
Is there a reason why Massachusetts allows this, but the rest of the nation does not?
The reason I ask is I have a design reviewer thinking that the NEC should override the MEC. But if that is the case, it wouldn't make sense that the MEC would even have this table in it, unless it were more strict.
http://www.mass.gov/eopss/docs/dfs/osfm/cmr/527cmr12-00.pdf
NEC values are more conservative than Massachusetts values. For 43 and above wires, Massachusetts allows 50% derates, while the NEC requires 35% derates.
Does this table apply to all circumstances where numerous conductors are in the same raceway, in Massachusetts? Both continuous and non-continuous loads, regardless if the circuit operation is simultaneous or diverse?
Is there a reason why Massachusetts allows this, but the rest of the nation does not?
The reason I ask is I have a design reviewer thinking that the NEC should override the MEC. But if that is the case, it wouldn't make sense that the MEC would even have this table in it, unless it were more strict.