I have a question concerning the definition of a branch circuit in the eyes of the NEC and how it correlates with how UL might interpret it. I am referring specifically to a piece of equipment listed under UL48 (Electric Signs). The electrical installation external to the sign would fall under Article 600. I will be referring specifically to 600.5. The electric sign is not incandescent, fluorescent, or neon. So, I would say that 600.5(B)(1) & (2) do not apply to this product.
However, UL48 16.1A dictates ?Signs shall not be connected to a branch circuit exceeding 20 amperes.? The manufacturer of this sign claims that they meet their UL listing requirements because the incoming wires are a ?Feeder? and not a ?branch circuit? as that clause literally states.
A little info on the sign: The incoming service lands to a termination panel which incorporates 20A single pole breakers that then distribute 20A single pole circuits out to the various power supplies and loads within the sign. The incoming circuit to the sign is sourced from a load center containing a three pole 50A breaker. This incoming circuit from that distribution panel is a three phase 208Y/120V, 4 conductors + gnd.
Thoughts?
However, UL48 16.1A dictates ?Signs shall not be connected to a branch circuit exceeding 20 amperes.? The manufacturer of this sign claims that they meet their UL listing requirements because the incoming wires are a ?Feeder? and not a ?branch circuit? as that clause literally states.
A little info on the sign: The incoming service lands to a termination panel which incorporates 20A single pole breakers that then distribute 20A single pole circuits out to the various power supplies and loads within the sign. The incoming circuit to the sign is sourced from a load center containing a three pole 50A breaker. This incoming circuit from that distribution panel is a three phase 208Y/120V, 4 conductors + gnd.
Thoughts?