On a typical control circuit protected by a fuse or circuit breaker, where you would have 120vac/125vdc running to a pressure switch and then energizing a solenoid valve, would a ground (in addition to the grounded neutral) conductor be required to be run in the entire circuit and this ground terminated at each device (pressure switch, solenoid valve)? This would be in a power plant environment.

[ August 17, 2005, 02:25 PM: Message edited by: BA Evans ]
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: NEC

Run in the entire circuit? Yes.

Terminated at the pressure switch? No.

Terminated at the solenoid valve? Yes.

You have to run the ungrounded (phase, or "hot" conductor) and the grounded (neutral) conductor together. But the neutral only has to be landed at the load (in your case, the solenoid valve).
 

physis

Senior Member
Re: NEC

You don't have to, but if you use the edit function to change the name of the "topic" of one your two threads it would be a lot easier to know which one's which.

If you click this icon
edit_ubb6.gif
you'll be able to edit your post.
 

redfish

Senior Member
Re: NEC

would a ground (in addition to the grounded neutral) conductor be required to be run in the entire circuit and this ground terminated at each device (pressure switch, solenoid valve)? This would be in a power plant environment.
Yes, you would be required to have an EGC ( equipment grounding conductor).If you are installing metallic conduit, this can serve as your EGC.
 