This is from their catalog on their website (Unistrut's website, that is):







Unistrut channel is listed by Underwriters' Laboratories as a surface metal raceway. Snap-in closure strip is used to complete the raceway. Accessory parts listed by Underwriters are noted on drawings.

Steve​
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I have used it as a raceway a number of times, mostly in industrial facilities.

With the particular manufacturers componets and plates you can install devices in it.

Roger
 

cadpoint

Senior Member
Location
Durham, NC
Are you kinding me!!! And I thought a cut in Box was tight.

Whats the derating on that, does one only use 40% ?

Ode to the forum ... :)
 

raider1

Senior Member
Staff member
Location
Logan, Utah
cadpoint said:
Are you kinding me!!! And I thought a cut in Box was tight.

Whats the derating on that, does one only use 40% ?

Ode to the forum ... :)

Take a look at 384.22 for the number of conductors permitted in strut type channel raceway.;)

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We use the Kindorf raceway quite often for lighting in commercial and industrial buildings. Almost the same as the Unistrut stuff.
 