K Khalid Ahmed Member Aug 12, 2008 #1 Is it a code violation to wire a four plex receptacle with 4 seperate circuits and a duplex with 2 seperate circuits?
Is it a code violation to wire a four plex receptacle with 4 seperate circuits and a duplex with 2 seperate circuits?
Buck Parrish Senior Member Location NC & IN Aug 12, 2008 #2 No, If you have 277 and 120 in the same box you will need a devider.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 12, 2008 #3 don't overlook NEC 210.4(B) & 210.7(B)
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 12, 2008 #4 Khalid Ahmed said: Is it a code violation to wire a four plex receptacle with 4 seperate circuits and a duplex with 2 seperate circuits? Click to expand... Every receptacle on a given yoke must be equipped to be disconnected simultaneously. If, by "four plex" you mean two duplexes, then each duplex must deenergize simultaneously.
Khalid Ahmed said: Is it a code violation to wire a four plex receptacle with 4 seperate circuits and a duplex with 2 seperate circuits? Click to expand... Every receptacle on a given yoke must be equipped to be disconnected simultaneously. If, by "four plex" you mean two duplexes, then each duplex must deenergize simultaneously.