cdriggers

Member
I have a prime generator suppling power to a building, first going to a MDP first means of disconnect, where at this point everything is grounded, as well as generator, I have 5 wires leaving MDP going to a buildings panel where the ground and neutral is seperated, do I need to add additional ground rod outside of building, and can I come from panel grd terminal to add cold water grd. I have looked in 250.32 and 250.35, just not sure if I need the extra grd, being the MDP is only 100ft away, thanks.
 
I have 5 wires leaving MDP going to a buildings panel where the ground and neutral is seperated, do I need to add additional ground rod outside of building, .

If this is an another structure different from the one where the first MDP is located you need to establish a grounding electrode system, and take the feeder egc to that grounding electrode system. (isolate the neutral at the second structure) (if thats what you aare saying)
 