You can infer from 240.3, that the overcurrent protection rules in Article 240 are not intended to protect equipment.
You can infer from 240.3, that the overcurrent protection rules in Article 240 are not intended to protect equipment.
I have to disagree here.
If that where the case there would be no reason at all for maximum overcurrent device ratings on equipment that the NEC requires us not to exceed.
Where in the NEC does it say that a circuit breaker protects wire insulation and not equipment? Thank you.
I don't agree. If the equipment is not covered by the articles listed in T240.3, then the NEC does not directly cover the overcurrent protection of that equipment. Overcurrent protection may be indirectly required by the application of 110.3(B)....
In short:: Use the article listed in Table 240.3 if your device is listed there; Otherwise use article 240.
Yes, and I said that Article 240 only covers the protection of the conductors. The articles you listed do require protection for equipment but those rules are not found in Article 240.410.153.
422.11.
427.57.
430.95.
440.21.
450.3.
455.7.
All specifically deal with overcurrent protection of something other than conductors.
That would not be an Article 240 requirement. It would be a 110.3(B) requirement.I have to disagree here.
If that where the case there would be no reason at all for maximum overcurrent device ratings on equipment that the NEC requires us not to exceed.
I don't agree. If the equipment is not covered by the articles listed in T240.3, then the NEC does not directly cover the overcurrent protection of that equipment. Overcurrent protection may be indirectly required by the application of 110.3(B).
That would not be an Article 240 requirement. It would be a 110.3(B) requirement.
With the exception of the rule in 240.13, I don't find any rules in Article 240 that require overcurrent protection for equipment.
Thanks for the replies. I have a client who wants to see a simple explanation in print aside of the NEC. I saw a code article in either EC&M or Electrical Contractor that gave a good explanation of circuit breaker protection.
Does anybody have a recollection of this article. I believe it was this year.
I have to disagree here.
If that where the case there would be no reason at all for maximum overcurrent device ratings on equipment that the NEC requires us not to exceed.
That would not be an Article 240 requirement. It would be a 110.3(B) requirement.
With the exception of the rule in 240.13, I don't find any rules in Article 240 that require overcurrent protection for equipment.
CF I cannot see it that way as often equipment or conductors are overloaded and the breaker opens before more damage happens,
Example: Branch circuit wiring is overloaded, breaker opens before the conductors become damaged. Remove overload reset breaker and we are back in business. The breaker protected the conductors from damage.
Example; a motor is mechanically held up, the overloads open before the motor is damaged the OLs protected the motor from damage.