I've got a soft serve ice cream machine it has TWO 30A twistlock recp on it from the factory. single phase 208-230. I have 240V, I assume I am fine since there is no 230V.
These are the markings for the two sides of the ice cream machine.
1) Min circuit ampacity. 23A
Max fuse 30A
2) Min circuit ampacity 28A
Max fuse 35A
On the side 2 I do not want to fuse at 35A. Would 10 awg and a 30A breaker be sufficient. Is that what is meant by min circuit. ampacity?
I also have a coffee maker with a 30A dryer plug on it. The coffee maker is 25.8 amps. Would you say a coffee maker is continuous? I would guess not, so 25.8A on a 30A breaker and receptacle should be fine, Correct?