Hello the following was provided via a manfacture of a machine for our plant.
I am using a 400amp breaker (from) a buss duct for this application
I have sized my wire at 500kcmil copper for this application.
Please I am second guessing my self on this. Thank you in advance for your responses
B. Mandl
ESA-10 (75kW):
Power during typical operation: 185 kVA 220 A at 3x480V,
Inrush current: typically, 450 A for 20 sec (max. 5 starts per hour),
Main Circuit Breaker: 400 A
I am using a 400amp breaker (from) a buss duct for this application
I have sized my wire at 500kcmil copper for this application.
Please I am second guessing my self on this. Thank you in advance for your responses
B. Mandl
ESA-10 (75kW):
Power during typical operation: 185 kVA 220 A at 3x480V,
Inrush current: typically, 450 A for 20 sec (max. 5 starts per hour),
Main Circuit Breaker: 400 A