Hi guys,
I just begin my power engineering career after graduation this August. I have worked in an engineering consulting firm for two months. I lack of working experience and I really need your help and advice for my design.
When I design panel schedule for residential projects.I just want to make sure the power output for some mechanical equipment.
When I see the equipment schedule, for example:
AC unit:
Fan HP:1/3
V/PH/HZ: 230/1/60
MOCP: 25
MCA: 17
Could you help me to check whether my understanding is correct.
Based on my understanding:
MOCP means maximum over current protection size. Therefore, the size of breaker is 25A/2P?
MCA means maximum current. Therefore, the maximum current is 17A.
For power output, I have two different understanding:
1. 1HP=1kVA, therefore the power output is 334VA.
2. Power output=Voltage x MCA=230x17=3910VA.
Could you tell me which understanding is correct?
Thanks
I just begin my power engineering career after graduation this August. I have worked in an engineering consulting firm for two months. I lack of working experience and I really need your help and advice for my design.
When I design panel schedule for residential projects.I just want to make sure the power output for some mechanical equipment.
When I see the equipment schedule, for example:
AC unit:
Fan HP:1/3
V/PH/HZ: 230/1/60
MOCP: 25
MCA: 17
Could you help me to check whether my understanding is correct.
Based on my understanding:
MOCP means maximum over current protection size. Therefore, the size of breaker is 25A/2P?
MCA means maximum current. Therefore, the maximum current is 17A.
For power output, I have two different understanding:
1. 1HP=1kVA, therefore the power output is 334VA.
2. Power output=Voltage x MCA=230x17=3910VA.
Could you tell me which understanding is correct?
Thanks