What is the best wiring method for a 100 Amps residential sub-panel (3+1 wires). The wiring path is more than 100 ft and requires several 90 degrees bends.
The new aluminum SER cable has a better aluminum alloy then the old aluminum cables and is not supposed to have the same problems as the old stuff.
Make sure your sub panel lugs are listed for 75 C or you MUST use the 60 C chart on 310.16 for 100 Amp feeders or less! 1/0 Al = 100 A
jeff43222 said:I just installed some #2 Al SER (2-2-2-4) recently. Is #1 a weird size? Why wouldn't it be available? I am admittedly fairly ignorant about Al wiring in general since I use copper as much as possible.
We did a number of apartment complexs in the mid-70s with the new alloy aluminum THHN wire and CO/ALR devices. There were no more problems it those jobs than with the ones we did using copper.The aluminum industry said it was fine for wiring back in the 60's and 70's too. Their claims didn't exactly play out the way they said. Give me copper.
don_resqcapt19 said:Larry,
We did a number of apartment complexs in the mid-70s with the new alloy aluminum THHN wire and CO/ALR devices. There were no more problems it those jobs than with the ones we did using copper.The aluminum industry said it was fine for wiring back in the 60's and 70's too. Their claims didn't exactly play out the way they said. Give me copper.
Don