If the load is fairly ballacned on the two non-grounded conductors then you should not have much current going through the neural, so voltage drop on it should not be an issue. e/m.pryan said:I have a 700 foot underground service circuit, 350 feet half way that will be carrying 100 amps, 240 volts, single phase. Do I also need to compensate for a voltage drop on the neutral wire (using aluminum wire )or just the line voltage wires?
Physis 3 said:I wouldn't even try to answer the question without knowing something about what the load or loads are.
Regardless, the answer to the question would still be: yes, voltage drop on the neutral must be considered, especially when it is sized to handle only the maximum imbalance between itself and any one ungrounded conductor.Dennis Alwon said:I totally agree. If this is for a panel with many 120 volt circuits then I would upsize my neutrals. If you have mostly 240 volt circuits then there may be no need to upsize the neutral.
pryan said:Do I also need to compensate for a voltage drop on the neutral wire (using aluminum wire )or just the line voltage wires?
If you have any 120V motors of any size (over 1/4HP), I'd greatly increase the size of the neutral, maybe even bigger than the phase conductors.
Grounding conductor yes, neutral no.danickstr said:if you upsize the UC's you have to upsize the neutral and Grounding conductor.
In the event of a ground fault, where the OCPD would be attempting to instantaneously interrupt the circuit in the magnetic portion of the circuit breaker, that '3/4" ball valve' is going to behave very similar to the '4" ball valve' in that scenario - but I like the way you think.danickstr said:i do not agree with the plumbing analogy given, because of the OCPD acting as a 3/4" ball valve