Done a VD clac and need some one to advise.
208/120 Volt 3 phase 4 wire 60 Hz
I= 1600A D= 300 FT. VD =3% Copper in PVC conduit 3 ft. under ground.
ambient is about 90 deg F.
Came up with 1 785.36 MCM
4 500MCM per line only does about 1540 Amps
5 400MCM per line is 1675 amps.
Assuming I dont have to be NEC compliant, which, if any, is right?
appreciatte any help.