Here is the setup. Single family dwelling, with 200 amp meter/main outside feeding main lug panel in basement. GEC from well casing to meter/main. Interior water piping must be bonded. I am under the assumption that the bonding jumper to the water piping must connect at the service disconnect as per 250.104 (A)1. Reading through to #3 Makes me wonder if I can connect to the EGC terminal in the main lug panel. Does 250.104 (A)3 read Multiple buildings or structures supplied by feeders, meaning multiple buildings or any structure, or does it say Multiple buildings or structures supplied by feeders, meaning multiple buildings or multiple structures?
Either way would you say that I have a stucture supplied by a feeder as the service would be the meter/main.