I left my code book at the house and cant find my ugly's book.:mad:Can someone look up what size conduit I will need for 3/0 tray cable (3 conductor with ground). The diameter of the cable is 1.42". The conduit will need to be Rigid. I think 2-1/2 or maybe even 3". Thanks in advance.
 
I left my code book at the house and cant find my ugly's book.:mad:Can someone look up what size conduit I will need for 3/0 tray cable (3 conductor with ground). The diameter of the cable is 1.42". The conduit will need to be Rigid. I think 2-1/2 or maybe even 3". Thanks in advance.

One cable diam 1.42 @ 53% = RMC 2".

Cable area 1.5837
Total area 3.408
Available to use @ 53% 1.806
 